  1. We want to put a cap on the highest voltage in the system, relative to earth. We know there is 230V between the two cables, but there may be thousands of volts between those cables and ground, unless you explicitly tie one end to ground. When you do that, you know one conductor is at zero, and the other is max 230V. Therefore we need at least one place in the installation where earth and neutral are tied together.

  2. We don’t want working current to flow on earth conductors. Only fault current is allowed on earth conductors/wires. Therefore you are only allowed ONE bonding point.

  3. There is already one (and only one) earth point in your installation. That is either an earth spike at the kiosk (TN-C-S earthing), or there is an earth spike at the transformer with an earth cable running all the way to your house (TN-S earthing). You use this earth for everything, this is the earth connection.

  4. Earth is already bonded to neutral by your supplier, either at the transformer (TN-S) or at the kiosk (TN-C-S). You are not allowed to bond it again.

  5. When the inverter goes into islanded mode, it disconnects both live and neutral. The neutral on the output of the inverter therefore becomes disconnected from the earth point. You want to reconnect it, so that you again have one (and only one) TN bond in the system, your max voltage in the system remains 230V, etc etc.

  6. Something counter-intuitive about fault current. The reason we earth the cr*p out of things, and ensure really low resistances, is because large fault currents is a good thing. Small fault currents suck, but large fault currents show that are is most definitely a fault. So in systems that are not protected by an RCD (such as inverters), you are relying on a good flow of fault-current to trip a breaker.

  7. Now without such a bond, in other words by leaving Live and Neutral floating, you won’t get a nice solid fault current. It is quite typical for the current carrying conductors to settle at roughly half the voltage, so now your highest voltage in the system is a random 120V or thereabouts (you can never be sure). Imagine a ground fault involving a human being as part of the circuit, allowing 15mA to flow. That is not enough to trip the RCD, but to is enough to give said human a nice jolt (but usually not kill him, unless he has a weak heart). If the system was bonded, contact with the live wire would cause 30mA to flow and trip the RCD. Still a nice big jolt, but now the fault was actually detected. Additionally, the neutral wire doesn’t shock. So while we often say we need the bond for the RCD to work, that is only half-true. The RCD still works without the bond… it just becomes a bit wishy-washy-undefined, sometimes we trip, sometimes we just tickle a bit.

Aaaanyway. So now we need to consider how big that bonding relay needs to be. It can switch 25A, but it can carry way more. I suspect the contactor will never actually have to switch the full fault current. The trouble is, I cannot guarantee that. In a fault condition, everything is off the table unless it can be guaranteed. Then I have to make provision for the maximum current that could occur in a fault situation.

So… that 25A contactor is probably okay. But I cannot guarantee it. And it might not actually sign off…

2 Likes

To continue that thinking. The bonding contactor is never closed while the grid is connected. It is always closed after the grid is disconnected, and it is always opened before the grid is reconnected. Therefore the maximum fault current it needs to switch, is the short circuit current of the inverter (which is roughly 200% of it’s max capacity). But that is still over 60A on an 8kVA inverter. So still no dice.

On a smaller inverter, if we could guarantee that the bonding relay will never be operated with the grid connected (which you can do, if it is integrated as in the Multi), then you could go smaller. In this case, I think it is clear that you need something bigger.

1 Like

My reading of the SANS regs is that it acknowledges that there is always some unprotected segment between the source and the protection device. This segment must be as short as possible and rated to at least the same as the protection device.

The EN bonding relay would be in this segment, so should be rated to the same current as the breaker on the output of the inverter.

And I guess that’s what all the suspect installers and diy guys assume as well. It works fine in 100s of installs… so it must be fine… or 10A has been fine for me so why do I need bigger…. Until something goes wrong.

I fail to understand why these shortcuts are taken. Percentage wise, how much more does the correct safety devices add to a 100k or 150k install. Almost negligible.

I guess the cost element is a part of it, I also guess for many installers they simply don’t know better. Even on this thread, it took quite a few posts for some pretty knowledgable guys to come to what seems to be an authoritative conclusion.

Am I right in saying there is agreement that the contactor/relay should be rated for at least the same as the breaker on the inverter output, and the cables sized accordingly?

Yes, that seems like a good conclusion. If you wanted to be pedantic, you could say it needs to match whichever is the larger breaker (input or output), but that would be just to cover the fault condition where the contactor is closed while the grid is connected AND there is a fault condition.

1 Like

Input breaker is 50A, so that’s not a problem in my case.

Would it solve the "problem“ if I put a 20A breaker on the N wire that goes to the contactor?

That would do the opposite of solving it.

2 Likes

Ok. Scrap that idea. It would keep the contactor from exploding but also kill the earth in the process

Yes. We never put a breaker on the earth / protection.

Communica sells a 40A relay that’s relatively cheap ~ R350 the last time I got one, can also be din rail mounted. That’s just a little over the rated current on the 8kw unit.

The 40A from AC/DC for R80 seems a bit suspect though.

During this entire conversation I was working under impression that a 63A contactor is not cheap. Which it isn’t, if it is a multi-pole thing like you’d use in a star/delta starter, but after actually looking, the Hager is about 1k (that’s for a 2P), ACDC has one for under R500 (also a 2P). Haven’t seen any 1P models, which is a little unfortunate… takes up more space in a DB.

You may think that you can just parallel the contacts of a smaller contactor to get the rating up, but because the contacts never engage or disengage exactly at the same time, that doesn’t work.

Found this guy lying around at the old man’s, but probably not much better than the contactor I bought yesterday?

What’s the current wisdom on the grounding of batteries? Is this something that needs to be done?

That refers to the cross sectional area of the earthing busbar (section 6.6.2.7, table 6.25).

The requirements for the cross sectional area of the earth conductor itself is significantly less:

Went live a bit earlier this evening. So far so good, nothing has burnt down or exploded yet.

1 Like

When my parents bought their first washing machine they watched the full 2.5h cycle on camping chairs… Of course we thought they were crazy when they told us :slight_smile:

Have fun, and stay safe!

1 Like

You should apologize in advance to your family for the hell you are going to put them through over the next few weeks while you try to optimize the system and cut down your grid usage as much as possible.

Oh, and good luck for the next cloudy day you experience.

1 Like

Fair point! Hope they play along nicely.

I am though hoping to have sufficient capacity to not worry too much about usage. Obviously having a zero grid consumption is ideal, but I’m not going to cry too much if we end up buying in a couple of units every now and then when the aircon runs a bit longer or the sun doesn’t shine.

1 Like

So month 1 was a good success. Managed 86% self production, cutting my bill down by a pretty hefty chunk.

Looking forward to see how the system dynamics change as we head towards spring.

1 Like

Very nice! You ended up going with the 8kW? What panels did you put in? That production is really good for a winter month.