280ah EVE cells, what are the best settings?

Would be nice if we all have similar cells, similar equipment, to agree on the best settings that we can all use and see how the banks perform over time, adjusting as needed.

My settings:

BMS:
Total Capacity: 280ah
Cycle Capacity: 224ah (80%)
Cell full voltage: 3.450v
Cell Minimum voltage: 2.900v
80%: 3.325v
60%: 3.275v
40%: 3.250v
20%: 3.200v

Balancer:
Start Voltage: 3.200v
Delta to Balance: 0.010v
Balance Only when Charging: Yes

BMV: … if one has one …
Charge Efficiency: 99%
Peukerts Exponent: 1.05
Charged Voltage: 0.3% below Absorption
Tail Current: 4% (~2 to 4%)
Discharge Floor: 20%
Charged Detection Time: 3 (~2 to 5 min.)

5kva MPII:
State of Charge when Bulk is finished: 95%
Charge Efficiency: 0.99
DC input low shut-down: 2.9v - 46.4v
DC input low restart: 3v - 48v
DC input low-pre alarm: 3.1v - 49.6v

Absorption: 3.55v per sel - 56.8v
Float: 3.4v - 54.4v
Charge: with 280ah, max inverter can do, 70amps
Repeat absorption: 1.00
Repeat absorption interval: 7
Absorption time: 1

With the 280ah EVE, I want to get it right … so with 17/18 cells, the above will have to be adjusted, as Victron can handle 38–66V, so methinks for 18 cel bank to go for 3.4v x 18 = 61.2v

I’m open for ideas, feedback, suggestions?

@Louisvdw is incorporating the BMV midpoint measurement, so an even number of cells will be better.
Also, in terms of physically arranging the cells, an even number is neater and more flexible.

In terms of tweaks, (if my understanding of @Louisvdw’s script is correct) is that at 98% of capacity the charging rate is hard-coded limited to 1 Amp. I think that should be equal to the balancing capability of the BMS. (Which I think is 160mA for the JBD BMS).
Otherwise, the highest cell voltage will still climb and result in a shut-off.

91 < SOC <= 95 then max charge amps = max_battery_current / 2
95 < SOC <= 97 then max = 4amps
97 < SOC <= 100 the max = 1amps

That’s the way I read it, at 1 Amp the charger will still gain on the balancing and even a few mA at the top end can cause a voltage spike.

And that is why I’m looking for confirmation that the BMS can disable the charge … IF I understand it right.

I’ve seen on my 12v MP, it drops the charge current, then it hits 98% and goes back to max charge amps, moment it hits 99%, it drops back to 1 amp.

We have no idea why … have made changes but no luck so far.

What IS interesting, on my old bank, it was just drama.
On these new 280ah cells, the delta stays perfectly in line …

Moral of the story … do not let the cells get out of balance … ever.

Matched and batched cells have their perks.

FWIW, I am starting to understand why brand names differ so much in their settings. It depends on what cells they are using and how many.

From that they work out exactly what the settings must be, to ensure longevity for “those” cells they opted to use.

So the ideal is to get to a point where if one uses like say 280ah EVE cells, with XYZ BMS, then set the system and BMS settings to so, and one should be sorted for a very long time.

We don’t have a clever highly trained department for that, but man, we do have a lot of experience here on this forum, to figure it out. :wink:

You can spesify a very small charge amount but that does not mean the charger can give you such a small limit. Initially when I did test I found that smaller that 1A makes no difference.

@Phil.g00 you comment about the midpoint graph does not make sense to me. With lithiums we have the values per cell. Any midpoint is just a fun graph for a lithium battery. You already have much better in the min/max cell graph.
Physical arrangement is easier with even numbers, but it is also doable with odds. 15 cells goes in nicely 3x5 (but nothing can help with 17 cells - you will have something off somewhere)

OK, good to know.

As you state this is probably redundant for most people, but it seems that you have encountered the request and are incorporating it, so I assume somebody somewhere wants it.

I was really addressing @TheTerribleTriplet suggestion of 17 vs 18 cells.
However:
The busbar arrangement gets messy adding the third row, two rows allows for neat +ve to -ve busbars. The first row of cells can turn back on themselves, but turning back for a third row the positive and negative terminals of the batteries are no longer adjacent.
Doable, but not as neat.

1 Like

This is what I mean by two rows being OK, but adding a third row of cells would not be as neat:
image

1 Like

I’m really not fussed about neat, are there any actual negatives to consider, effects on the cells?

I assume not … but I rather ask.

A 17 cell bank alternative is your own suggestion, what advantages are you fussed about that make this a better choice than an 18 cell bank?

Nothing other than the cost of one more cell …

YOU are the one who started this 18 cell thing! :laughing:

And we “bought it”, hook line and sinker, as it makes 100% sense, large ah, running it “lightly”.

Brandnames with 15 x 100ah cells in, I think we are putting together the mother of all banks.

Another “joke” we make is if one has:
18 cells, and for whatever reason, one goes, take it out.
17 cells left, so another one goes as you now realize “o my, what did I do”.
16 cells left … "why me!?
… can take one more out for a 15 cell 48v bank.
:wink:

Yes, and I am still am in favour of 18, over 17.

Must admit, the Virgo in me don’t like odd numbers … :wink:

This next order, I’m getting 18, and 16 to sell on.

I didn’t consider numerology or the astrological angle in my reasoning.
But if you want to go there:

Right, BMS settings, who has an opinion for 280ah EVE cells?

We are, for sake of ease, talking 16 cell bank here.

Default settings for LifePo4 on JBD BMS’s.

Cell Over Voltage: 3.65v
Cell Minimal voltage: 2.80v
Cell Under Voltage: 2.500v

Cell Capacity:

  1. Cell full voltage: 3.500v
  2. 80%: 3.400v
  3. 60%: 3.350v
  4. 40%: 3.300v
  5. 20%: 3.100v

Balancer Configuration:
Start voltage: 3.200v
Delta to Balance: 10mV

I used the 150ah cell settings from before, o man, the 280ah cells did NOT get to 3.5v per cell. Have to redo them all.

Technically I’m a Virgo too (if you believe that stuff), and I kinda like odd numbers. What I like more than odd numbers are prime numbers. I like them because I know other people tend to avoid them, so they make numbers that tend to be unique. Especially useful when you’re choosing subnets for your internal networks, with the future potential for VPNs and bridging such networks, I’m pretty sure there are comparatively few people out there running 172.16.13.0/24, because 1) for some reason 10.0.0.0/8 and 192.168.0.0/16 are more popular, and 2) people tend to not like 13… :slight_smile:

1 Like

Don’t give me food on a plate that is not in pairs … and I like 192.168.0.xxx

Palindromes! I spot palindromes on car number plates while driving.

For other things to keep you awake at night, look at the Collatz Conjecture, or the Hilbert Hotel.

But back when I picked a subnet for my home, I somehow picked 192.168.8.0/24, because I thought it would be faster to type (you already have one finger on the 8), completely forgetting that 10.0.0.x is even faster…

So yeah… different day, different rules. Spotty consistency.