Sunsynk 8kw export to grid when set to zero export?

the pictures… can i believe them?


Its normal to see a 50-100w value to the grid even when set to 0.

During hybrid mode, the relays basically connects the grid to your essentials. So its not impossible some power gets leaked back to the grid while the inverter tries to match the load on essentials and non-essentials. Its a micro controller, there is still some latency between measuring and controlling the generated power.

This is an over simplified explanation, its probably far more complex than that.

phew, thanks @tinuva , just thought there is something amis with the CT, just double checked on the inverter itself…
looks good