MultiPlus II Settings & Optimisation

Seems like it works when charging from the grid. PV charge current is not limited.

@wernerhp Are you MPPT’s set as Networked? Check in the MPPT settings…

image

There are a list of MPPT firmware, etc requirements as well to get things correct here: 11. DVCC - Distributed Voltage and Current Control

What Mark said … if I reduce the DVCC amps, the MPPTs are also throttled. The entire system is “throttled”.

Yes, but that only works when DVCC is on. If it doesn’t work, then something else must be wrong. I’ve been drowning in support this last week, so I’m leaving it for you guys to figure out.

Oh, if you have the option enabled to feed excess DC-coupled PV into the grid, then it also doesn’t apply any limits.

1 Like

@mmaritz Looks like it. I didn’t fiddle with any of this yet.

The battery charges very erratically.