Interesting issue with panels

I got called to a member of this forum to assist with a F23 error on a Sunsynk.

Normally F23 means that the inverter is sensing a leakage on something like the PV the PV wires. Previously we found wires that got caught between the panels and the rails, or even wires that got damaged where they go through the roof, but at this client we could not find anything wrong with the wires.

He is experiencing alarms early mornings, late afternoon and then up to 22H00 in the evenings. Once the panels starts producing, he wont experience a problem again.

I had all three wires from the panels to the combiner box disconnected and did a few tests. Meggered the wires and the lowest recorded reading was 110 M Ohms on a 1000 volt setting. So no problem there. Then I tested the voltage per panel, adding 1 by one till all strings were connected and saw that each panel gave 45.5 volt although the VOC rating was 43.2V. This was done late afternoon and I would not expect a VOC that high. The last test was interesting. I measured between earth and Positive and got a reading of 42volt. Earth to negative was 0V. I then decided to measure that “Leakage voltage” again starting from a single panel and adding one by one after recording the reading. Each panel i added contributed just over 5 volt to the reading. I have never seen something like this before and this morning I decided i would try it in my own installation. 2 x 400Volt strings and 4 x 200 volt strings. I could not find any DC component between Pos-Earth or Neg-Earth.

At the client, I thought maybe if i connect the panel earth to the council earth I would get rid of the leakage, but when i did, the reading went from 42 volt to 20 volt.

Anyone here that can maybe explain this as I have never seen this in all the years i have been playing in this field. All i know is that he has some unknown panels that i have never heard of before and can only suspect that the panels might be the cause here but don’t know how to prove that.

Good morning Jaco,

is the 20v you see, AC or DC?

Morning stok. Its DC.

Can you swap out or remove the suspect panel? If the fault goes away, you can prove that the problem is with the panel. I don’t know how that would be possible, because there should not be any path from the panel connections to the frame?

And then once you have the panel on the ground, you can do more thorough tests.

The problem is, its not one panel. Each of the 8 panels add about 5v to the total of 42 volts. I added one by one to the series string and the value increased with everyone i added.

That indicates something else is amiss. Usually this sort of thing happens when the backing cracks and the panels are wet, then there is leakage to the rails. What happens when you disconnect all the panels (measuring DC and megging to rails).

Thinking about it, it could also be some sort of capacitive coupling.

I disconnected all and did an insulation test. Lowest reading were around 110 mega Ohm on a 1000 Volt setting.

Can you easily eliminate the cables as a problem - by replacing them? And can you check the MC4s for missing orings?

His installer used Ingle panels and claimed its the same quality as Canadian. I have never heard of this brand and cant find much on the internet.

This Facebook link will show you more of the quality of Ingle range.

Yeah, it’s probably not really worth trying to fix it an any other way than replacing with a recognizable brand. I don’t know why anybody still buys random brands? It would still be interesting to find the actual cause.

The client suggested we replace the panels, but I was not comfortable selling him new panels only to sit with the same issue after replacement. I have 8 x 450 JA solar in my warehouse and will repeat the test later today using them. If i can be sure that the panels are causing the issue, I can test the panel to better understand the issue.

Of course there is the risk of DC breakdown on solar cells (if you push too high a voltage across them in reverse), but if it wasn’t for that… or if you didn’t care too much about the panel, I wonder if one can just megger them from each power cord to the frame. That will tell you if it leaks… I am just concerned that it might also damage the panel? Something to research a bit. Maybe at 250V you can get away with it?

Breakdown voltage, in reverse, is usually at least 10V per cell, so depending on where the short is and how many cells are between the short and the cable you are testing. Of course it also depends on current, the small amount of current a megger puts through there, for a short period, may not be damaging at all.

Anyway, I am speculating. Maybe someone knows.

Edit: Looks like you can megger them. See video:

I presume the soapy water is better at ingressing and providing continuity into any cracks in the panels??

1 Like

Some late feedback. We tried what we could but could not stop the F23 on the sunsynk for this client. No issue for a week or two and then its back. A while back the client asked that we replace the old no name brand panels that were installed by someone else. I was not comfortable selling him 8 new panels before I could confirm that it is indeed the panels and not an internal Sunsynk issue. Three weeks back we removed the old panels and installed new panels for the customer and it seems that the problem is gone.

He wanted to then use some of the old panels to heat his geyser and we moved them to a different roof and pulled in a new string to an Elon smart on the geyser. I received an whatsapp from the customer today with the following screenshot.

The insulation issue now moved to the Elon Smart. This smart controller seems to be smarter than I thought, being able to monitor DC insulation breakdowns as well.

1 Like

Very interesting for the Elon to also pick it up, would have thought it’s another feature a manufacturer can brag about in their marketing material.

Had to Google what DC Insulation failed means … explanation had this pic:
image

Impressed that it is being tested for …

Does Victron MPPT’s also test for such? Will there be an error code?

DC insulation testing is legally required in most countries for DC voltages > 120V. So only cheap inverters intended for sale into 3rd world countries won’t have it.

Many countries are starting to require arc fault detection too, so pretty soon it will be hard to find inverters without that either.

1 Like

The RS products do (Multi-RS, MPPT-RS). The smaller MPPTs do not.

1 Like