Help needed with 2 X Multiplus 48/5000/70-48

Hi, I have two problems I need help with please:
Equipment:
2 X Multiplus 48/5000/70-48 units in parallel
4 X Revov 1st Gen B100 1C batteries
1 X Victron Cerbo GX
1 X Victron BlueSolar Charger MPPT 150/100
9 X Jinko 550W panels

Problems:
1: When Escom is not available the system maxes out at about 3400W. Overload protection kicks in and system shuts down. As if only one Multi capacity is available.
2: MPPT not supplying power to the critical or non-critical loads when Escom is available.
Example:
If Escom is on, Escom supplies the bulk of the critical and non-critical consumption. The solar production is severely limited. Production from the solar is less than 400w if the batteries are full.
If I disconnect Escom the solar production increases and supplies the 3000W needed for the critical side.

What am I missing?

Carlo Gavazzi ET112, yes, no?

Hello Jaco

Yes.

I have no experience with MultiP’s in parallel, but theoretically your panels (even if optimally angled) have roughly 5000W Pv, but in real live (my system at least) you could deduct 1-1,5 Kw from that due to losses etc.

So your production seems on par.

Mppt’s are only there to charge the batteries so what your system can produce is not limited by them.

Is this not some of the new software upgrades/functionality we now have that is not set correctly? There’s quite a few new features which I don’t understand fully yet. Peak shaving power being one of them I seem to recall.

How up to date is your software?

This reads a wee bit difficult?

MPPT’s are there to provide all they can.
If solar is not enough, batteries are used.
If still not enough, or min SOC is reached, Eskom is used.

Agreed, but their basic function is to keep batteries happy and if full, to supply the loads.

Point I am trying to make is that if batts are full the MPPT can still deliver a 100 DC amps in theory for conversion to AC and use by the inverter. With the system the OP has, an MPPT is not really going to be the limiting factor here.

MPPT should supply all it can if the loads are high enough, and then the system will be limited by what the inverter can produce, which in turn is dependent on what the BMS will allow in terms of battery discharge.

I believe the issue is software related.

When Dion gives me access, I will have a quick look.

For I agree, it is software settings and/or firmware related. I can make a quick check for the obvious.

If not, then Dion will need more help for I don’t do parallel systems. Victron is very clear about that. One needs in-depth knowledge. Hope it gets solved with the quick check.

Not theory, fact. :slight_smile:
I do that every day. SOC is 100%, set to Keep Charged actually.
At the time the panels produce the max the MP needs to heat geysers. At times >4kw.
Little to nothing goes to the batteries.

Caveat:
Also the spot with Lifepo4 that when a big load goes off, where must the power (±4kw) go for those few seconds on a charged Lifepo4 bank before MPPT’s throttle back?
Also why I stop at 3.45v max charge.
BMS has so “headroom”.

It could be that some of the settings on the different units differ? Resulting in some miscommunication?

Possibly the Multi’s is / must also be configured as with multiple batteries, ie a master and a slave?

He has a nice system there, but its not performing as it should given his observations.

Are you sure it is overload protection, or is that a guess? You’ve ruled out the possibility that the batteries may drop out on voltage if worked hard? Is the shutdown immediate, or does it take some seconds/minutes?

Even a single 5kVA unit should not max out at 3400W, it should be able to push a constant 4kW.

Are you using ESS? Is the ESS mode set to Keep batteries charged or something else? Is the battery full at this point? Do you have DVCC enabled? Very important to check all that.

The MPPTs do their own thing, they aim only for the voltage they have been told by the battery (via the GX). If the battery voltage reaches the target, the MPPT will stop charging. The system should create a small difference in the voltage target to prioritise solar energy, and it is possible something is going wrong there, but first it is important to make sure all these other things are set up correctly.

Also, as a diagnostic step, what happens if you enable the option to feed excess DC-coupled PV into the grid (in this situation where PV seems limited), does the solar chargers ramp up and the energy is fed into the grid, or not?

Hi

Let me try to answer questions as good as I can.

1: Are you sure it is overload protection, or is that a guess?
That is the message in the alarm logs.

2: Is the shutdown immediate
More or less immediate.

3: Are you using ESS? Is the ESS mode set to Keep batteries charged or something else?
Yes, Optimized (without BatteryLife)

4: Is the battery full at this point?
Full

5: Do you have DVCC enabled?
Yes

6: what happens if you enable the option to feed excess DC-coupled PV into the grid
I am to scared to enable this. I do not want to feed back into the grid.

This is my current state. I know for a fact that the panels will produce +3000W if I switch off Escom.

If I switch off Escom now the system will stop on overload.

Jaco is having a look now. Hopefully a problem can be identified.

Checked all, seems fine.

Changed under ESS:
Peak Shaving, Above Min SOC Only.
Multiphase regulation, Total of all phases.
… because mine is so.

But this:
Inverter settings - look at the red block, the charge voltages and the max charge amps, on a 400ah battery?
image

MPPT settings:

My Rule of Thumb, MPPTs and inverter must be the same settings.

Found this too …


Contact my connection as I suggested. I’m not touching this parallel thing. :rofl:
Remember to check the 50a max charging on 400ah Revov bank.

You have a wiring issue! I took the liberty to log into that site and look at the power distribution.

Right now, you have almost 4kW flowing through the slave unit, and almost nothing through the master.

You need to check that your parallel wiring is properly connected to both inverters, and of a similar length/resistance. Although in this case it is like at least one of those wires are completely disconnected…

1 Like

Calling on Dion to immediately rush home to inspect the cabling!

Don’t make us wait!

I am rushing!! Two speedfines. Checked all connections, cabling and lenghts. All fine. Supplier suggests faulty Multiplus.