I currently cannot increase the Grid Current Limit (GCL) above 15A on my GX device.
Newly paralleled Multiplus II’s - VE Configure value set to 50A so that is correct - been repeated 2x already… I thought I was mistaken initially.
It looks like ESS (is it?) is overriding my select value so even if I increase the GCL to 25A it stays at 15A (ie 30A for the system, 2x 15A for each MP)
I may be missing something
Yes: I know 30A is about 7000w so it could also be a limit from the BMS/MP’s capacity/etc - I am just wondering about the reason.
I have set it up and tested it… TOU tariffs inputted etc. I’m sure you can use it…
If you have a TOU meter I guess it will work - waiting for mine in the new year at some stage…
Oh hang on, I’ve seen this! You’re using the peak shaving option, right, and that is set to something lower? I noticed that for some reason the shore current limit override sent to the Multi also affects the AC current input. I reported this to the developers involved as well. Check the firmware changelog for the Multi firmware, I think that’s where the issue is? I can also do it later…