Depending on who you ask, you will be given some number between 30% and 70%. I think it is much closer to the lower end, and this paper seems to concur, placing it at “about 35%”.
As I understand it there are two factors behind this.
The first and most prominent is that your single-speed compressor has a very high start peak (as much as 500% of its nominal power), and there are higher losses associated with that kind of inrush.
The second has to do with the energy needed to create a state change in water, in this case specifically the water vapour in the air. The energy needed to cool water down is linear up to the point where it changes state (from gas to liquid), when the energy requirement shoots up. An intelligent air conditioner can avoid cooling below the dew point, which affects the relative humidity inside the room and requires a lot of energy. It is unclear whether the average split-AC even has a dew-point sensor, but in some hvac systems it is a component.
(That is also why you don’t crank the AC down to the lowest it will go, if that is below the dew point, the AC might spend a lot of time essentially turning air into water without making the room any cooler).
Yes, for a floor space of about 15 squares, 9kBTU is sufficient.
This depends. When you sell the house, the sparky will tell you in no uncertain terms that this does not comply, and you must immediately rectify the situation at the cost of thousands to install a new breaker.
My understanding is that this is not necessary. First, if we consult our copy of SANS-10142, that classifies an air conditioner as a “fixed appliance”, that’s a device that cannot be moved without using tools.
You are allowed to have mixed circuits up to 20A, that is, fixed appliances can share a plugs circuit:
6.15.4.3 essentially requires an earth leakage, and 6.16.3.2.3 is about cooking appliances. For air conditioning and heating, if the device needs more than 16A, then it must have a dedicated circuit:
But a 9kBTU air conditioner is going to run at more like 3 to 4 Ampere.
You must however make it possible for the AC to be disconnected (for servicing), which means either the plug needs to be accessible to the technician, or you need to install an isolator:
And this disconnector should be within 1.5 meters of the outdoor unit, in a waterproof box probably:
And finally, you can’t have it on a multiplug adapter. You can however replace the socket with one of those dual-socket outlets, and designate one of them as the permanent power of the AC:
That’s my understanding of how it works, but I am not a sparky, and if I am wrong, then I will accept information to the contrary.