What breaker for a geyser

Recent new DB’s installed, the sparkie followed his training, i.e. lights and geyser before RCD.

Saw it, whilst he was busy, and asked him to put the geyser and lights after the RCD please.

But nuisance tripping’s, he said.
Yes, I’m aware. If that starts happening one day then I will know that something is not right. I will then identify which circuit and we will sort it.

As of Today:
3 x Eskom and 3 x Critical Load DB’s in this house.
Each of the 6 DB’s have a 63a RCD’s for my protection.
2 newer DB’s, all are wired after the RCD.

Main Eskom DB from the street, when we do the entire house CoC early 2025, the geysers will be moved to after RCD too.

Be careful of lights on a RCD. Not required, and CFL/florescent lights will cause havoc…

Granted. I did quote from a very new version of SANS-10142. The 2009 version of that document says simply this:

6.16.2.1 All water heaters shall be bonded in accordance with 6.13.

Nothing about an RCD.

For myself… I would change it. I’ve heard stories of people getting a tickle from the shower.

Currently there are a few CFL/florescent bulbs left. So far no problem in the last few years.

It is a thing when a plumber does not bond the geyser properly.
That CoC one needs for a geyser.

True, but this is one of those cases where, while electricity takes the shortest path… not all of it does that. So when you have an element that has corroded to the point that it is making electrical contact with the water, and the water not being entirely sterile, then the vast majority of the current will of course take the shortest route to the metal tank (which is grounded), but a small amount, probably in the <1mA range… is going via the copper pipe and the water through the human being in the shower…

1 Like

I see the requirement for an RCD in the 2017 edition. Perhaps that was the year it was added.

3 Likes

Well if you change anything on your installation after the new regulations, you would have to change it to be compliant anyway. But apart from that, your geyser and pipes should be hard-strapped to earth so a trickle should not be possible unless you also have another fault.

From what I recall the regulations changed for the safety of plumbers, not the end-user… (after some grim stories)

1 Like

In that case, he needs to update his training…

3 Likes

It boggles my mind how someone can be in a trade and not make any effort whatsoever to keep up with the regulations that govern it.

2 Likes

Jip.

Not a scientific poll but in my experience since ±2018 with various Installation Electricians, now and then even a Master Electrician or two, the ones that can haul out the latest regulation book released (onsite on request), them having been on the update course, maybe 1 out of ±20. It is not cheap to get the book and do the course.

What then follows, the interpretation of what that latest book says, when it is not absolutely clear.

Hence I read all these post with attention, and where I’m unsure, ask the people I trust off forum, for their opinion.

Then I present that knowledge of how I want it done to the sparkie doing the work, and the good ones, they make work of that information.

The ones who don’t, argue with no book in hand, have asked one or two to leave the premises too.

It is the wild west out there.

Since this thread started, I have on three installations, installed an earth leakage on the stove and geyser, even though there were none to begin with. Left lights on the the no earth leakage circuits.

The stove is not required to be on RCD. In fact you will see in the manual of some say that if you do so, it will cause nuisance trips.

1 Like

Can nuisance tripping be caused by a fault that should be sorted out ??, to be on the safe side ?

2 Likes

Sometimes…

Loads with a poor load factor, like florescent lights, large motors, or even a large number of PCs can cause nuisance tripping. This is not a fault - it is a real lag in phase current, which the RCD detects and trips on.

So it is not always something that can be ‘fixed’.

2 Likes

No disagreeing, but I think one must first consider a fault, as @Tariqe posted.

If there is absolutely no fault whatsoever, then one can fall back to the loads causing the issue.

“Never attribute to malice (PC’s/FCL’s etc) that which is adequately explained by incompetence (actual faults)”. :grinning:

How would that work? An RCD just checks that the current on neutral is the same as the current on live.

In modern houses the biggest cause of nuisance trips are the class Y caps in SMPSs that connect to earth. (and surge protectors, that have essentially the same arrangement.) The solution is RCBOs.

1 Like

Can’t guess what this stands for…

RCBO stands for Residual Current Circuit Breaker with Overcurrent Protection. It’s a safety device that protects electrical circuits from overloading, short-circuiting, and earth leakage currents. RCBOs are a vital component of electrical systems and are installed in consumer boards or fuse boards.

An RCBO protects electrical equipment from two types of faults; residual current and over current. Residual current, or Earth leakage as it can sometimes be referred to, is when there is a break in the circuit that could be caused by faulty electrical wiring or if the wire is accidentally cut.

Basically combined RCD and breaker. You have one of them for each circuit instead of a breaker and delete the main RCD.

I believe in some oversees markets RCBO’s is basically standard if not mandatory. What does our codes say about their use?

It will be a bit expensive to redo the entire DB all at the same time, but a interesting option.