The datasheets specify the maximum wire size, but they do not explicitly say you cannot insert two of a smaller size. I would like to know where he got that information. The clamps of both these open wide enough so that you can easily stack 2 x 16mm2 wires on top of each other.
i am not good at marking up photos but i can easily explain. All black neutral wires except the 2 ones coming from the inverter (inverter grid and inverter back up which are protected by 50A CB’s) are offending because they are only protected by the 60A main switch. They are all 10mm2. All the red wires are ok they are all 16mm2 (except the 2 coming from the inverter grid and inverter back up (only 10mm2 but protected by 50A CB’s) and the top RCD which is also only 10mm2, because i ran out of 16mm2 when i prepared the board for the new install and instructed the installer to upgrade to 16mm2. Until this is done this wire is also offending)
There is still a mistake with the wire protection of the alternative power supply (UPS) indicator light. the wires must be changed to 10mm2 because they are only protected with a 50A CB (but that is another story and does not need to be debated in the thread)
nice . Much easier, than to try to squeeze a 10mm2 wire into a Hager indicator/pilot light. Thinking about this i thought about the redundancy requirement for indicator lights. If for example the little fuse blows or the indicator light breaks, then there is no longer any visual indication, that there is an alternate power supply to the DB board. Is this ok?